[Shop-talk] unsafe wiring
    Rich White 
    rlwhitetr3b at hotmail.com
       
    Sun May 10 18:36:31 MDT 2009
    
    
  
Does your wiring have two or three insulated conductors?
The bare wire should NEVER be used to carry current.
That being said, the DPO of our house did that and I have not corrected that
circuit yet.
If the conductors are black, white and bare, just move the white to the
neutral bar where the bare conductor should already be and you will have it
wired to code.  You should also change to a single breaker which is really not
any harder than moving the wire.  Get the correct size for you application.
Rich White St. Joseph, IL USA
'63 TR3B TCF587L
That ain't a scrap pile, that is my car!
See it moves!
> Date: Sun, 10 May 2009 15:02:54 -0700
> From: cak at dimebank.com
> To: shop-talk at autox.team.net
> Subject: Re: [Shop-talk] unsafe wiring
>
> Pat (and Donald, who replied directly):
>
> Thanks - that's a great idea. I don't know why I didn't think of it.
> Indeed, the original wiring used Romex, so I have a white lead. I
> can either change out the double-pole at the breaker or just leave
> it as is with one pole disconnected...
>
> I'm not sure there's a neutral bus in the subpanel, but it doesn't matter;
> there's only one circuit there.
>
> So.. what about using BX under the eaves?
> _______________________________________________
> Support Team.Net http://www.team.net/donate.html
>
> You are subscribed as rlwhitetr3b at hotmail.com
>
> Shop-talk mailing list
>
> http://autox.team.net/mailman/listinfo/shop-talk
>
> http://www.team.net/archive
    
    
More information about the Shop-talk
mailing list