[Shop-talk] AC compressor is tripping 20A breaker
    Jeff Scarbrough 
    fishplate at gmail.com
       
    Sat Jul  9 19:37:55 MDT 2011
    
    
  
On Sat, Jul 9, 2011 at 6:30 PM,  <shop-talk2 at mcfetridge.org> wrote:
>
>
> Any thoughts?  Suggested steps to investigate the issue?
1.  20 Amps is pretty small for a central air conditioning compressor.
 But no reason to believe it's undersized.
2.  A circuit breaker that trips due to overload will only flip
halfway or less.  It should be between on and off, in the middle
position.
3.  If it trips when starting, it's possible you have a bad starting
capacitor.  But if it trips and leaves the handle in the "On"
position, I'd suspect a bad breaker.  These ~usually~ cost between $5
and $10 -- a cheap enough thing to replace and see if it helps.
Is the trip consistent, or intermittent?
Jeff "Reddy Kilowatt" Scarbrough
Corrosion Acres, Ga.
    
    